Well sort of. A detached garage needs a main or six throws to disconnect the structure-- same as a service. You may have an amendment.john1 said:Montgomery cty Ohio inspection department require a main be put in the
sub-panel in a garage at a dwelling giving code article 225.30
correct or wrong John1
fireryan said:I dont think I understand the 6 thrown thing. would someone please explain this to me?
Wrong article reference.john1 said:Montgomery cty Ohio inspection department require a main be put in the
sub-panel in a garage at a dwelling giving code article 225.30
correct or wrong John1
2008 NEC
225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section. the requirements in 230.6 shall be utilized.
Exceptions irrelevant and omitted for brevity
john1 said:to me rule 225 is a commercial rule and should
not be applied to single family dwelling rules .
john1 said:One person pick up the right issue he stated the article was wrong and he is correct. You need to look at more 225 rules to see requiring a main at each building , rule 225 is a rule use for more then one building on single property. a garage at a single family dwelling is not a second building .
john1 said:225.36 even state the the rule requiring a main in second building has a exception for a garage at single family home dose not apply. Just a bad inspector abusing his authority in my opinion.
:-?john1 said:....to me rule 225 is a commercial rule and should
not be applied to single family dwelling rules...
2008 NEC
225.1 Scope.
This article covers requirements for outside branch circuits and feeders run on or between buildings, structures, or poles on the premises; and electrical equipment and wiring for the supply of utilization equipment that is located on or attached to the outside of buildings, structures, or poles
II. More Than One Building or Other Structure
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E).
For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
john1 said:........I thought that had some good people out there....... Just a bad inspector abusing his authority in my opinion........
john1 said:Montgomery cty Ohio inspection department require a main be put in the
sub-panel in a garage at a dwelling giving code article 225.30
correct or wrong John1
Disconnecting power for a service or separate building can be done with a single disconnect or up to 6 disconnects (couple of exceptions)fireryan said:I dont think I understand the 6 thrown thing. would someone please explain this to me?
john1 said:Montgomery cty Ohio inspection department require a main be put in the
sub-panel in a garage at a dwelling giving code article 225.30
correct or wrong John1
john1 said:I thought that had some good people out there that would help me
support my thinking on the code and rule 225 at single family dwelling and a bad electrical inpector / department for enforcing rule 225 on dwelling.
Sometime the NEC is not very clear on what it is saying and you need to add
some words to make it clear, to me rule 225 is a commercial rule and should
not be applied to single family dwelling rules .
john1 said:You need to look at more 225 rules to see requiring a main at each building , rule 225 is a rule use for more then one building on single property. a garage at a single family dwelling is not a second building .
john1 said:225.36 even state the the rule requiring a main in second building has a exception for a garage at single family home dose not apply. Just a bad inspector abusing his authority in my opinion.
Dennis Alwon said:You may have an amendment.
triplstep said:And as previously stated, some ahj's have added further provisions to the nec.
You're reading the wrong section, and even then, I don't see how you came to your conclusion. See 225.33john1 said:Hillbilly look at rule 225.36 exception, garage dose not apply to rule 225
Stickboy is correct, if you're reading training material that says something different you should probably throw it away.john1 said:Stickboy their are many training manual that have residential, commercial and industrail rule of NEC Ray Mullian has a commercial book for NEC
You're still reading and trying to apply the wrong section. See 225.33john1 said:Mpd 6 disconnect dose not appy to garage sub-panel 226.36 exception
Charlie is correct, you are wrong. See 225.33john1 said:Charlie no six disconnect rule at a garage apply, not a service to garage
john1 said:Hillbilly look at rule 225.36 exception, garage dose not apply to rule 225
Stickboy their are many training manual that have residential, commercial and industrail rule of NEC Ray Mullian has a commercial book for NEC
Celtic Stallcup electrical design book clearly show how rule 225 is to be used
Mpd 6 disconnect dose not appy to garage sub-panel 226.36 exception
Charlie no six disconnect rule at a garage apply, not a service to garage
john1 said:O.K. I give up , let stop the talk and do the action. I'm Electrical inspector
you are a electrical inspector we are going to court
I'm going to state you are violating house bill 175 abusing your authority
provide document NEC 2008 page 70-71 225.36 except 225 dose not apply
page 225.38 exception rule dos not apply to garage. I'm also going to provide Stallcup picture on how to apply rule 225 to commercial job. also Ray Mulllin residential wiring book with over 400 Residential code rules that apply to residential wiring no items listing 225 rule and a garge wiring in residential book with 614 pages .
These documents will be provide to the Judge to aid his discision , what are
you going provide to show rule 225 dose apply to residential garage wiriing ??