john1 said:
sorry that answer won't win in court . I onlly want answer that are code article to win in court ,code article that tell me I need a main in panel at garage at a dwelling .
"..... need
a main ....."
It's actually
1 to 6 disconnects that are needed. . 225.36Ex1 is an exception to the general rule [225.36] which requires a rating of "suitable for use as service disconnect". . The 1 to 6 disconnects still applies in
all situations and the snap switches, stated in the exception, are counted toward that total.
225.36Ex is an exception to 225.36.
225.36Ex is
not an exception to 225.31 or 225.32
225.38Ex is an exception to 225.38.
225.38Ex is
not an exception to 225.31 or 225.32
"..... main in panel at garage at a dwelling ."
The "main" at the dwelling is the required
overcurrent. . Don't mix up main/building disconnect with main/building overcurrent.
The
overcurrent for the second building/garage and the conductors supplying that building are in the
dwelling.
"code article to win in court", 240.21
The 1 to 6
disconnects for the second building/garage must be in the second building/garage
itself.
"code article to win in court", 225.32 + 225.33
john1 said:
O.K. I give up , let stop the talk and do the action. I'm Electrical inspector
you are a electrical inspector we are going to court
I'm going to state you are violating house bill 175 abusing your authority
provide document NEC 2008 page 70-71 225.36 except 225 dose not apply
page 225.38 exception rule dos not apply to garage. I'm also going to provide Stallcup picture on how to apply rule 225 to commercial job. also Ray Mulllin residential wiring book with over 400 Residential code rules that apply to residential wiring no items listing 225 rule and a garge wiring in residential book with 614 pages .
These documents will be provide to the Judge to aid his discision , what are
you going provide to show rule 225 dose apply to residential garage wiriing ??
"225.36 except 225 dose not apply
page 225.38 exception rule dos not apply to garage."
225.1 tells you to follow everything in 225 for power run between buildings.
225.36Ex + 225.38Ex apply and are counted toward your 1 to 6 disconnect limit.
As others have told you, snap switches have an amperage limit, so if you supply the building with a feeder than is larger than the amp rating of the snap switch, then your snap switch is in violation.
"Ray Mulllin residential wiring book with over 400 Residential code rules that apply to residential wiring no items listing 225 rule and a garge wiring in residential book with 614 pages ."
"code article to win in court" ? . Ray Mullin isn't code !
No matter what Ray Mullins says, the code section is 225.1
"These documents will be provide to the Judge to aid his discision , what are
you going provide to show rule 225 dose apply to residential garage wiriing ??"
The judge will check with Ohio law that lists the National Electrical Code as state law and does
not list Ray Mullin as state law.
NEC wins, he'll rule according to 225.1 which states that the other parts of 225 also apply.