Gar-- if you install a 60 amp main breaker in a sub panel and wire the feeder conductors to the breaker then, IMO the wire is protected from overload. The 100 amp breaker will protect it from short circuit faults and the 60 amp will indeed protect the wire from overload. How can you have more than 60 amps on the wire if there is a 60 amp breaker ahead of the load?081105-2144 EST
A 60 A breaker at the load end of the cable does not protect the cable. This 60 A breaker only protects the wiring or load following the 60 A breaker.