Sub-panels in basin area

Status
Not open for further replies.

phil

Member
Location
Kansas
Had an electrician install sub-panels in master bedroom clothes closets, and we are requiring him to relocate these panels. On the opposite side is a small room than contains a basin. A door off this small room leads into the toliet/shower area. Would the basin area be considered part of the bathroom area?
 
Re: Sub-panels in basin area

As long as the bathroom is separated from the "basin room" by a door, I would say it is ok to install a panel in the room providing there is proper working clearance for the panel.
 
Re: Sub-panels in basin area

NEC 2002 Article 100 - Bathroom. An area including a basin with one or more of the following: a toilet, a tub, or a shower.
 
Re: Sub-panels in basin area

So if the basin area has a door separating it from the other fixtures are they in another area?
 
Re: Sub-panels in basin area

How about the definition of a bathroom by the Uniform Plumbing Code? A room equipped with a shower or tub. I do realize we can't mix the two codes to make something fit. Ron
 
Re: Sub-panels in basin area

A room with just a basin is not a bathroom.

Bathroom. An area including a basin with one or more of the following: a toilet, a tub, or a shower.
It sounds like there is a door separating this area with a basin from the toilet and tub.

IMO this is not a bathroom.
 
Re: Sub-panels in basin area

Ryan you let a counter top outlet go without GFCI as you considered it outside the kitchen when there where no walls to separate the area.

Now when we have walls and a door you would like to extend area right through the walls.

Sorry Ryan, you said you expected to get hammered and who better to do it than a friend. :D
 
Re: Sub-panels in basin area

Does 230.70(2) cover subpanels, or any panel that doesn't include the service disconnect?
 
Re: Sub-panels in basin area

If this is not a bathroom then there is no need for GFICs or a 20 amp circuit in the basin room or the tub, toilet/shower room.

I think the bathroom "area" would extend beyond the door. If the definition of bathroon use the word "room" instead of "area" then I would agree it would not be a bathroom.

Russ, see 240.24 (E)for overcurrent devices.
 
Re: Sub-panels in basin area

If a door changes the required location,then does height of the receptacle do the same thing.Like an outlet 8 ft on a plant shelf for a TV,since in a regular room over 5"6" does not count as a required receptacle then it should not apply to a bathroom either.
 
Re: Sub-panels in basin area

The NEC uses the words area for a bathroom so that putting a door around any of the parts of the bathroom for privacy does not change requirements, the handbook ( this is reference not code) shows several different configurations.

Having doors for privacy does not make a bathroom not a bathroom.

tom
inspector
 
Re: Sub-panels in basin area

Thanks to all that answered. We decided it was in the bathroom area and are requiring them to be relocated somewhere other than the closet or bathroom. Your input is greatly appreciated.
 