hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
If it is a threewire pump using the breaker to turn it on would accomplish nothing but a fried pump, if the start winding was left energized all of the time it would overheat and the motor would quickly fail, if the start winding was left disconnected the motor would quickly fail. The only way this would work is if it is a two wire pump that has everything self contained in the pump, but with the readings that you took, it should be a three wire. If you gamble and buy a control box, get at least a 3/4 hp box, (about $50) and wire it color for color to the terminals.( they will have B (black) R (red) Y (yellow) next to the screws. If the pump runs for awhile, then the overload trips, then you know you have a larger pump. If you can, take the amp readings while it is running, and match those with the pump manufactures specifications to calculate the HP of the pump. If it doesn't run , you could have a bad pump. The inside of the control box will tell what values of resistance you should have between each wire.