ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
One thing that absolutely makes sense is that the sum of 1.25X the maximum output currents from multiple inverters should in no case be more than the rating of the busbars in an AC combiner panel. Modules are so inexpensive these days that inverters are frequently loaded to the point where the maximum AC output current is likely to be reached and maintained for hours from time to time.I guess I am still not understanding why its not "sum off all load devices". IT seems very simple and more consistent with electrical theory. IS there a situation I am missing when it fails?