I want to hang 8' flour lights from a ceiling I found in the code you could go 5' between supports so does that mean that i could have 5' of pipe between fixtures without any supports
			barbeer said:Are you looking in the 02?
iwire said:Even if you apply the '5 foot' rule you need at least one support.
Meaning if the fixtures are 10' apart or 1' apart you would still need a minimum of one support between the fixtures.
raider1 said:No 358.30(C) is new to the 2008 NEC. This section was added to clarify that EMT may be unsupported between enclosures for lengths not exceeding 18"
Chris
iwire said:OK then I should change my response to
If the fixtures are 10' apart or 18.1' apart you would still need a minimum of one support between the fixtures. :smile: