Surge protectors work by turning electrical energy into heat. The surge protectors in the panel reduce the energy in the surge, leaving a much smaller surge for the point of use protectors to deal with. Surge protectors installed in the panel are NOT useless. To provide good protection both panel and point of use protectors should be used.
In combination I would agree. The marketing is “whole house” implying that one little $100 surge arrester protects everything, with or without point of use protection. If you are at all concerned though skip the whole house arrester unless you put in a substantial one.
But there are two glaring issues. The first one is line length. Surge arresters are NOT the same as say fuses. It does not protect “downstream devices”. An arrester is wired in shunt or parallel to the devices. It is in series with the leads going to the load. So the voltage as seen by the load is the voltage across the surge arrester PLUS the voltage across the leads.
As approximate formula for the lead voltage is:
Vlead, kV = 0.34 (microhenries/foot) x length (feet) x di/dt x 2 where di is the surge crest current in kA and dt is the time to crest in microseconds.
So say we trip a breaker with a 25 kVA transformer with a 2%Z. That’s 25 / 240
/ 0.02 or 5.2 kA short circuit current and the surge will be maybe 1.5 times that by utility estimates or 7.8 kV. Switching surges will be 100 KHz or more or about 10 microseconds. So if we are 10 feet from the main panel that’s 20 feet of length (count hot and neutral). So we get:
0.34 x 20 x 7.8/10 x 2 = 10.68 kV or 680 V. We have to then add this to the MCOV of the panel surge arrester at a common rating of say 175 V so final surge is around 10-11 kV. If the surge arrester is right next to the load so we have say just 1 foot away to a wall wart, then by the same math lead surge voltage is only 0.53 kV and we are at an easily survivable 705 V, 530 for the cable and 175 from the cheap power strip.
If the point was to take the surge possible at the panel from the utility transformer (tens of kV) down to 10 kV for the power strip then to 700 V for the load, mission accomplished. Without the panel arrester the power strip does the heavy lifting and has a shorter life. But going the other way, I stand by my statement that the panel surge arrester is worthless.
Second beef with panel surge arresters is that the name brand ones are little better than power strips. You can save substantial money putting a receptacle on the side of the panel and just plugging a power strip into it! It just looks impressive.
Take those components apart and physically compare it to what you find taking apart a power strip. Then compare those to say a MacLean Z-Force or Surge Tec surge arrester.
www.macleanpower.com
This is what utilities put out on the transformer. You should consider why they use one of these instead of that cute thing with lights and a device the size of the quarter that it costs. Just saying...big difference.
I have no affiliations with MacLean. I buy their products through supply houses. It’s just a brand that I know pretty well. Cooper and GE products aren’t as compact for panel installs. The SOLA stuff isn’t bad either. If the actual element doesn’t look like a “J” fuse it’s not worth much.
To find the little $0.25 MOV which is the same one you find in the power strips and in the Square D and AB products you need to look on the electronics web sites (Mouser, Digikey, Allied, Newark). It’s fine for point of use but not much else. Size does matter. The fatter the better.
Hence my beef with most of the whole house surge arresters on the market is the way they are sold. They are basically distribution equipment right at the demarcation line between feeders and service entrance. Just as the system bonding jumper and ground rods are important safety equipment to both feeders and service entrance, so is the panel surge arrester if one is used. You wouldn’t use a #16 ground wire (Code or not), why use a dinky one time use surge arrester? And if surges are actually important why protect the one part of the system that has a better chance of survival (higher BIL) when the loads fail all the time as another poster stated? And if you look at the math it’s obvious why they fail if surges are the culprits.