Well, everything has resistance, bonded or not.Well technically it is no longer bonded if the path is opened or gains resistance.
I was just pointing out, one may think everything around a pool is bonded, but then still have meter readings for potential diff. That falls into realm of no bonding and/or faulty bonding. Which may be the case for OP.
Or, some hot wire became exposed to the water, which creates potential diff to any grounded wire and likely the bonding, because most times the bonding is tied somewhere to ckt EGC.
Or, the bonding itself is in contact with hot wire via direct or indirect contact, and the tingle is between "everything that is bonded" and something that only touches grounded CCC or the EGC.
And then the other question to ask, is the power to this pool on GFCI?
Yes, I stated the obvious, but worth stating.