I have not heard about that addendum and I seriously doubt that will happen.
Not sure you will find an article that permits a 15 amp switch on a 20 amp circuit but the NEC is a permissive code and if it doesn't state that you can't then you can. Think of it this way-- why would you need a 20 amp switch if the load on the switch is less than or equal to 15 amps. If you have a 20 amp load on the switch then you would need a 20 amp switch[/QUOTE
What if the load changes after the initial install? You think all electricians are going to check the switches and make sure they are rated for 20 amps if they tack on some lights to a switched light loop? A respectable one would, but not all. A great deal of the code is in place because of the idea that future expansion may occur. This is my line of thinking anyway. I always thought that section of 210.21(B)(3) was odd and kind of goes against all kinds of other rules. Just my opinion I guess.
We don't live with "What if's". What if the electrician adds more circuits and overloads the circuit? What if the electrician takes a 6 disconnect rule on a service and adds a 7th disconnect?
The NEC is not supposed to be a design manual although it does tend to do just that at times. It is up to us to design a safe system. Now if you feel more comfortable with a 20 amp switch then go ahead and do that. I can say that I have done many many homes with 20 amp circuits and 15 amp devices and never had an issue.