All,
I'm reviewing a new service that will have a 600A main breaker at the main distribution panel. On the line side of this panel will be a CT cabinet with a 600A disconnect that is manually operated in case the service ever needs to be dumped from outside of the building (i.e. fire department in an emergency situation). I believe that this disconnect and CT cabinet will be two separate enclosures adjacent to each other.
I typically have electricians install the ground electrode conductors to the first point of disconnect and bond the neutral to ground for the system there. However, in the past the first point of disconnect has always been a breaker in the meter socket or at the main panel.
My question is, should I treat this manually operated disconnect as the location for the neutral-ground bond and the landing point for the ground electrode conductors or should this action take place at the main distribution panel where the first breaker (600A) resides, with an equipment ground conductor run back to the manually operated disconnect?
I'm leaning towards the latter.
Thanks,
Creig
I'm reviewing a new service that will have a 600A main breaker at the main distribution panel. On the line side of this panel will be a CT cabinet with a 600A disconnect that is manually operated in case the service ever needs to be dumped from outside of the building (i.e. fire department in an emergency situation). I believe that this disconnect and CT cabinet will be two separate enclosures adjacent to each other.
I typically have electricians install the ground electrode conductors to the first point of disconnect and bond the neutral to ground for the system there. However, in the past the first point of disconnect has always been a breaker in the meter socket or at the main panel.
My question is, should I treat this manually operated disconnect as the location for the neutral-ground bond and the landing point for the ground electrode conductors or should this action take place at the main distribution panel where the first breaker (600A) resides, with an equipment ground conductor run back to the manually operated disconnect?
I'm leaning towards the latter.
Thanks,
Creig