This issue came up in the following scenario i have service 4#750kcmil copper into service rated fire pump ats/controller/disconnect all in one.
The conductors label x in attached sketch on the load side of service rated fire pump ats/controller/disconnect all in one feeding the fire pump ground cable size the co worker is
saying cannot be larger than Table 250.102(C)(1) main bonding jumper.
Please note the conductors X is on the load side of service rated fire pump ats/controller/disconnect all in one is equipment grounding conductor.
Should it not be based off of Table 250.122? Also the breaker trip can be different then breaker frame size since its inside the fire pump controller/ats/disco/.