ceb58
Senior Member
- Location
- Raeford, NC
Back up and read post 37. Those 20 Kw units come with a 100 amp breaker. It doesn't matter if it is only capable of 83 continuous amps, the conductors that WE install must be sized to the OCP. If it is a factory whip then that is something different.My point is that the conductors between the gen. and the load should be large enough to carry the entire capacity of the generator's output, load diversity has nothing to do with that at all. Example, if you have a maximum load of 50 amps connected to a gen. that can supply a maximum of 80 amps what size conductor would you install? The answer should be conductors that can carry 80 amps.