Table 310.15(B)(7) clearly shows 2/0 XHHW-2 aluminum for a single phase dwelling being rated for 150a. Per the manufacturer the Aluminum is rated 90deg at 150a. Now the inspector claims the lugs of the load center (1st means of disc after meter can) are rated 60deg or 75deg. Because of this the inspector claims the 2/0 aluminum is now rated using 310.15(B)(16) 75deg column now 2/0 XHHW-2 is only rated for 135amps.
What is the rating for 2/0 XHHW-2 al when used as feeder wire to a building? And if the 1st means of disc is a meter main combo (ie feeding the ac from that panel before feeding the building) does that change anything?
What is the rating for 2/0 XHHW-2 al when used as feeder wire to a building? And if the 1st means of disc is a meter main combo (ie feeding the ac from that panel before feeding the building) does that change anything?