david
Senior Member
- Location
- Pennsylvania
I agree with you, you want to submit a change proposal? This section is supposed to change in 2014, but I think we will still have same question for the example you gave if using 2014 language.
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(3) Individual Dwelling Unit or Mobile Home Conductors. Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors. (Paragraph 310.15(B)(6) )shall be permitted to be used for conductor size.
Lets make it look something like this:
215.2 Minimum Rating and Size.
(A) Feeders Not More Than 600 Volts.
(3) Individual Dwelling Unit or Mobile Home Conductors. Feeder conductors for individual dwelling units or mobile homes need not be larger than service conductors. (Table 310.15 (B) (7)) ) shall be permitted to be used for conductor size.
Exception: when adjustments for temp or other corrections apply the feeder conductor size shall be adjusted according to those adjustments or correction factors
Last edited: