brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
I hear you but I’d think the code would supersede spec.

Anyway, my spec(or drawings) does not indicate anything about using afci at all but on the returned/rejected submittal they said to use them. I’m guessing(before I inquire about the rejection) they are going to cite NEC code.

What you’re looking for is a dual-function receptacle; it has both AFCI & GFCI. I have some that P&S sent me to sample but I’ve never used them.

Send a change-order along with your submittal update.


Sent from my iPhone using Tapatalk
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I would ask the contractor to use tamper resistant receptacles either way.
Afci not required by the nec and nyc amendments imho.
Nor gfci protection.
It’s common in nyc for electrical contractors not to be aware of 517.13 A and B so I recommend you follow up on this one.
Your saying that AFCI not required but the pic you posts requires it and it's the 2008 which NYC is following.
 

kwired

Electron manager
Location
NE Nebraska
2020 NEC added patient sleeping rooms in nursing homes and limited care facilities to places that need AFCI protection. If you are only on 2008 in this application then AFCI is only required in dwelling units AFAIK.

GFCI protection regardless of what year NEC applies would typically depend on other conditions at the location, areas like bathrooms, near sinks outdoors and such might require GFCI. Just being a psychiatric facility isn't enough information to otherwise dictate the need for GFCI.
 