Look at the pic above I posted.
Afci required in more areas than bedrooms.
What year NEC is that picture from?
Look at the pic above I posted.
Afci required in more areas than bedrooms.
2008 it seems.What year NEC is that picture from?
I hear you but I’d think the code would supersede spec.
Anyway, my spec(or drawings) does not indicate anything about using afci at all but on the returned/rejected submittal they said to use them. I’m guessing(before I inquire about the rejection) they are going to cite NEC code.
Your saying that AFCI not required but the pic you posts requires it and it's the 2008 which NYC is following.I would ask the contractor to use tamper resistant receptacles either way.
Afci not required by the nec and nyc amendments imho.
Nor gfci protection.
It’s common in nyc for electrical contractors not to be aware of 517.13 A and B so I recommend you follow up on this one.
Is this in a dwelling unit?Your saying that AFCI not required but the pic you posts requires it and it's the 2008 which NYC is following.
No psychiatric facility.Is this in a dwelling unit?
So forget the AFCI it is not required.No psychiatric facility.