Hi
My question is about my installation of a tandem 20 amp breaker (panel accepts them), using 12 gauge wire (1 black, 1 red, 2 neutral, 1 ground) through 1/2 inch emt to a double pole switch in 4 inch square surface mount metal box, then a 3 inch run of 1/2 emt to a 4 inch square surface mount metal box containing two 20 amp duplex receptacles. Total emt run is less than 10 feet from panel to receptacles. Each receptacle has it's own 120 v circuit and both are controlled by the double pole switch.
It's not a multiwire circuit so no tie bar is required, but I'm thinking I should put one on anyway for safety sake in case one receptacle faults but the other in the same box stays hot, thereby being a danger to work on if not caught at the panel by a knowledgeable person.
Is there any problem with putting a tie bar across both handles on the tandem breaker? Is there any issues that I'm not aware of with this installation?
Thanks
Kevin
My question is about my installation of a tandem 20 amp breaker (panel accepts them), using 12 gauge wire (1 black, 1 red, 2 neutral, 1 ground) through 1/2 inch emt to a double pole switch in 4 inch square surface mount metal box, then a 3 inch run of 1/2 emt to a 4 inch square surface mount metal box containing two 20 amp duplex receptacles. Total emt run is less than 10 feet from panel to receptacles. Each receptacle has it's own 120 v circuit and both are controlled by the double pole switch.
It's not a multiwire circuit so no tie bar is required, but I'm thinking I should put one on anyway for safety sake in case one receptacle faults but the other in the same box stays hot, thereby being a danger to work on if not caught at the panel by a knowledgeable person.
Is there any problem with putting a tie bar across both handles on the tandem breaker? Is there any issues that I'm not aware of with this installation?
Thanks
Kevin