A different thread prompted a question.
Assume a scenario where we have a 200 amp feeder and we tap that feeder with a 23 ft tap feeding a 50 amp breaker.
240.21 tap rules require that the tap conductor ampacity be 66.7 amps.
Would a #6 THWN-2 be acceptable in this situation ??
That conductor has a 90° ampacity of 75 amps and the load side device will limit the "operating" current to 50 amps.