hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
How long are the conductors from the 400 amp disconnect to the inside panels?
about 12 feet
How long are the conductors from the 400 amp disconnect to the inside panels?
Is 12' greater than 10' and less than 25'?about 12 feet
Is 12' greater than 10' and less than 25'?
2023 NEC TXI have townhome residential that has 400A fused disconnect with 400A fuses outside on the front wall of the townhouse and tap conductors are being brought in Panels A and Panels B. They are about 12 feet in length.
My question is that should 25 feet tap rule apply here or outside tap rule apply here?![]()
The only thing the 10' rule gives is the permission to use a smaller conductor, but in this case the tap conductor minimum size is based on the load end 200 amp OCPD.Likewise, if the conductors were 8 long instead of 12, you could use the 10' rule, the 25' rule, or the outside rule if you can meet all the requirements. As others mentioned, the conductors may not be nearest point of entry, so that option is out. Between the 10' and 25' rules, if you meet the conditions for both it doesn't really matter which rule you're using. You only need to comply with one to have a legal tap. If you want to skimp on something to force use of the 10' rule and not meet the 25' rule, you could if the conductors we're 10' long or less.
They're not parallel conductors because they are not connected together on both ends. Yes they meet the definition of tap conductors.Is this a tap conductor or parallel conductors? I dont see where tap conductors come into play here.
Gotcha, so if I were to do a 400A service and have (2) 200A panels off the 400A disconnect, I'm limited to 25feet ?They're not parallel conductors because they are not connected together on both ends. Yes they meet the definition of tap conductors.
If the tap conductors are inside of the building then yes. If they're outside and can meet all of the rules for the outside tap rule then they can be unlimited in length.Gotcha, so if I were to do a 400A service and have (2) 200A panels off the 400A disconnect, I'm limited to 25feet ?
But one could run say parallel 4/0 aluminum to near the panelboards and then use the 10 foot tap rule to each panel, however I believe you still need tap conductors rated no less than the overcurrent device being supplied so they would still need to be 250 aluminum or 3/0 copper for the taps.Is this a tap conductor or parallel conductors? I dont see where tap conductors come into play here.
Sent from my Pixel 7 using Tapatalk
That raises the question of why the tap rules are written in a way that is incompatible with 240.4(B) in the first place.But one could run say parallel 4/0 aluminum to near the panelboards and then use the 10 foot tap rule to each panel, however I believe you still need tap conductors rated no less than the overcurrent device being supplied so they would still need to be 250 aluminum or 3/0 copper for the taps.
If the tap conductors are inside of the building then yes. If they're outside and can meet all of the rules for the outside tap rule then they can be unlimited in length.
Yes. So if the tap conductors are OUTSIDE and then come inside the building into panelboard and total length tap conductors from the outside tap to inside panelboard are greater than 10 feet but less than 25 feet then one can use 25 feet tap rule?
You either have the misapprehension that (a) when the tap originates outside you must use the outdoor tap rule or (b) the 25' tap rule cares whether the conductors are inside or outside, or maybe both.Hold on i am confused. In my case tap is outside and i have outside tap conductors coming into building. The total length of outside tap conductors + inside tap conductors is 12 feet. How come you all are saying i can use 25 feet rule?
You have already been told, or shown enough to conclude with only minimal logic, that the 25' tap rule applies. About 5 times.Anyone?
You either have the misapprehension that (a) when the tap originates outside you must use the outdoor tap rule or (b) the 25' tap rule cares whether the conductors are inside or outside, or maybe both.
Neither of those is true. The installation satisfies the requirements of the 25' trap rule. As the OCPD supplied is not nearest the point of entrance of the tap conductors, the installation does not satisfy the requirements of the outdoor tap rule.
You have already been told, or shown enough to conclude with only minimal logic, that the 25' tap rule applies. About 5 times.
Cheers, Wayne
The diagram in the OP appears to show a service supplying the dwelling unit, so 225 Part II would not apply.Regardless of tap rule does 225.31 not require a disconnect nearest the point of entrance?