tap of panel bus

Merry Christmas
The SF on the part number translates to sub feed lug. These are used to provide a set of feed thru lugs on residential panels that dont have them. When used like that, a 150A subfeed lug cant be in a panel with a main larger than 150A. I have not read the documentation for these to know if they can be used as a feeder tap. Electrically, I dont see a reason why not as the downstream 150 would keep the lug within its rating. But this is not a proper feeder tap if it is not terminated in a breaker.
 
The SF on the part number translates to sub feed lug. These are used to provide a set of feed thru lugs on residential panels that dont have them. When used like that, a 150A subfeed lug cant be in a panel with a main larger than 150A. I have not read the documentation for these to know if they can be used as a feeder tap. Electrically, I dont see a reason why not as the downstream 150 would keep the lug within its rating. But this is not a proper feeder tap if it is not terminated in a breaker.
Yes, so that's the question. Is this limited to panels where there an upstream OCPD is 150 amps or less? Or can it be used for a tap that terminates in an OCPD 150 amps or less.
 
I see it that way only if the terminal block was rated for 200 as the main is 200. I think most are in agreement here. I think what I am going to do in the short term is use a 125 amp breaker and wire to feed the sub panel. There is no provision for a main at the sub so tap rules will not work. Hopefully in the spring the customer will allow a service change to correct all the other issues. At least it will be compliant on this issue.

If the terminal block was rated for 200 amps and the conductors connected to it were rated for 200 amps it wouldn't be a tap to begin with.

What is the violation of having a 150a rated terminal block used as a point for a tap?

The problem I see in this scenario is the lack of an OCPD in the subpanel being fed.