tap of panel bus

Merry Christmas
The SF on the part number translates to sub feed lug. These are used to provide a set of feed thru lugs on residential panels that dont have them. When used like that, a 150A subfeed lug cant be in a panel with a main larger than 150A. I have not read the documentation for these to know if they can be used as a feeder tap. Electrically, I dont see a reason why not as the downstream 150 would keep the lug within its rating. But this is not a proper feeder tap if it is not terminated in a breaker.
 
The SF on the part number translates to sub feed lug. These are used to provide a set of feed thru lugs on residential panels that dont have them. When used like that, a 150A subfeed lug cant be in a panel with a main larger than 150A. I have not read the documentation for these to know if they can be used as a feeder tap. Electrically, I dont see a reason why not as the downstream 150 would keep the lug within its rating. But this is not a proper feeder tap if it is not terminated in a breaker.
Yes, so that's the question. Is this limited to panels where there an upstream OCPD is 150 amps or less? Or can it be used for a tap that terminates in an OCPD 150 amps or less.
 
I see it that way only if the terminal block was rated for 200 as the main is 200. I think most are in agreement here. I think what I am going to do in the short term is use a 125 amp breaker and wire to feed the sub panel. There is no provision for a main at the sub so tap rules will not work. Hopefully in the spring the customer will allow a service change to correct all the other issues. At least it will be compliant on this issue.

If the terminal block was rated for 200 amps and the conductors connected to it were rated for 200 amps it wouldn't be a tap to begin with.

What is the violation of having a 150a rated terminal block used as a point for a tap?

The problem I see in this scenario is the lack of an OCPD in the subpanel being fed.

Jap>
 
I think the issue is, if there are conductors that are terminated in a 200A OCPD, but they run through a terminal block only rated to 150A, even though the 150A taps could be terminated properly, the terminal block could still have feed through amperage above its rating.

Did I understand that correctly, OP?
 
I think the issue is, if there are conductors that are terminated in a 200A OCPD, but they run through a terminal block only rated to 150A, even though the 150A taps could be terminated properly, the terminal block could still have feed through amperage above its rating.

Did I understand that correctly, OP?
You did. The lack of a main OCPD in the panel, 150 amps or less is the issue since the rating of the tap block could be exceeded.
 
What good is the terminal block if it cannot be used for a tap in a 200 amp or greater panel? With a 150 amp rating it would need to be used for a tap or not used at all when the panel was over 150 amps.
I suppose if it had a main breaker in the panel it was installed into then it would be fine. Without having the spec on this panel it may have a max load per buss stab as well. Personally I have never seen these used as a tap from a 200 a main. These are no longer made in a 150 amp rating.
 