Came across something I have never seen before and want some input.
We have a 400A MLO panel directly fed from a DTT. The panel is old and there are no breakers available to purchase to add in the panel. So, the thought is to tap the existing feeder and add a separate, 100A panel. If the tap is more than 10' but less than 25', 240.21(2)(1) says "the ampacity of the tap conductors is not less than 1/3 of the rating of the over-current device protecting the feeder conductors."
In this case, there is no OCPD so how would you determine what size the tap conductor should be?
Thanks for any discussion this may generate.
Steve
We have a 400A MLO panel directly fed from a DTT. The panel is old and there are no breakers available to purchase to add in the panel. So, the thought is to tap the existing feeder and add a separate, 100A panel. If the tap is more than 10' but less than 25', 240.21(2)(1) says "the ampacity of the tap conductors is not less than 1/3 of the rating of the over-current device protecting the feeder conductors."