I have a main 208V 3-phase, 3000 amp switchboard with sections V, W, X, Y, and Z
I need to tap the switchboard to feed 3-phase chiller loads with a total of 2100MCA that is more than 25 feet away from the tap. This means that I need 8 sets of 3#500kcmils (full size 3000A copper feeder to comply with the tap rule). I will use this feeder to feed a new 3000A switchboard which will feed the chillers.
8 taps for phase A will be at section V
8 taps for phase B will be at section W
8 taps for phase C will be at section X
section Y (a 3000A switch) feeds sections V,W, and X
As you can see, I am proposing to tap at different switchboard sections to feed the new 3000A switchboard.
Is this code compliant or must the taps be from the same switchboard section?