Thats what I did I just wanted to confirm im seeing that right it can be used now even if you dont need it for flexible connections is how I interperet it havent had to do it since 2017 so i believe it changed correct?! In other words i can run it everywhere in cable tray in a class 1 div 1 area let me know if thats how you interpret it.See 501.10(A)(7) in the 2023 code
In other words as long as I service and maintain it and its in an industrial plant not exposed to physical damage i can use it?Thats what I did I just wanted to confirm im seeing that right it can be used now even if you dont need it for flexible connections is how I interperet it havent had to do it since 2017 so i believe it changed correct?! In other words i can run it everywhere in cable tray in a class 1 div 1 area let me know if thats how you interpret it.
Ill be supervising itWhile the rule does not use the exact works, It would be my opinion that the facility that the cable is installed in would have to comply with the definition of Supervised Industrial Installation as found in Article 100.
And the facility complies with all of the other parts of the definition?Ill be supervising it
YesAnd the facility complies with all of the other parts of the definition?