Technical Feasibility of Underground AC Transmission Cable Grid

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Steal them from other sites and paste them. Go crazy!
run1.gif


Wait, you can do that?
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
Us hams call it Hardline
Curiously enough, they call it "Flex" and also offer a line of rigid transmission line. It bolts together like high-pressure flanged steam pipe.

hardpipe.jpeg
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
They also have rectangular waveguide which has no center conductor as coaxial waveguide or cable does. It will only propagate signals above a certain "cutoff" frequency, whereas coaxial (i.e., TEM mode) will propagate all the way down to DC.
Optical fiber is a circular dielectric waveguide which also has an associated cutoff frequency below which electromagnetic waves will not propagate.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Couldn't they keep cost down by direct burrying that cable? You know, 138kv URD?
The pipe isn’t the problem or the driving factor for cost.
Pipe is relatively cheap.
You don’t want to bury this type of wire 3’ deep and walk away.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Why can't that be done? Burrying 6 feet and walking away?
Think.

basically your lifeline to several hundred thousand customers is installed without supplemental protection.
Someone digs, bores, or drills into it.
Your major asset is too unprotected. This isn’t an hour fix.
NC had a drill go through a line like this and it was in a sound. You would think no one would be anywhere close to it.

Took MONTHS to fix
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Think.

basically your lifeline to several hundred thousand customers is installed without supplemental protection.
Someone digs, bores, or drills into it.
Your major asset is too unprotected. This isn’t an hour fix.
NC had a drill go through a line like this and it was in a sound. You would think no one would be anywhere close to it.

Took MONTHS to fix


Well, you'd have multiple circuits. So loss of one is not an issue.

Protection adds cost.

Direct burial with a red ribbon on top makes it a lot cheaper.
 

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I know you said "cost aside", but it's hard to get past the cost difference between underground and overhead. If you've ever done a cost estimation for a new MV utility feed where overhead vs underground was evaluated it is quite significant at times. Even for small and short MV services it can be tens of thousands of dollars for underground vs next to nothing for overhead.

I'd probably agree that outage frequencies may go down... but the duration of the outages when they do occur could go in the opposite direction, so your outage-hours could be relatively the same or worse. And now everything was just more expensive.



Disagree, with a networked or dual feed approach the duration is eliminated. These often have auto transfer on the primary gear:

 

bwat

EE
Location
NC
Occupation
EE
Disagree, with a networked or dual feed approach the duration is eliminated. These often have auto transfer on the primary gear:

So now we're talking underground everywhere and everything networked or dual feeds. Cost is obviously a factor in the way things are, but if we're playing the game where it is not, why stop there though. We could concrete encase everything and have detailed GIS maps on every inch that is always 100% accurate.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Well, you'd have multiple circuits. So loss of one is not an issue.

Protection adds cost.

Direct burial with a red ribbon on top makes it a lot cheaper.
So, how deep would you have to go to make it unlikely someone would jam a backhoe into a 500kv line? If there was a fault to ground from one of these feeders, how wide an area would develop a lethal step potential?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The pipe isn’t the problem or the driving factor for cost.
Pipe is relatively cheap.
You don’t want to bury this type of wire 3’ deep and walk away.
My neighborhood has 11kv underground feeds, they buried them under the sidewalks about 4’ down. The underground transformer for a big chunk of my neighborhood is in my yard and is basically under water whenever it rains. Apparently one on the connectors leaked one winter and allowed water to seep into the insulation where it eventually migrated down into the conductor. The result was an explosion that lifted the sidewalk concrete up about a foot in the air. It took a crew of 4 guys 4 days to fix it and test it, not counting the concrete crew that replaced the sidewalk. I was working from my home office at the time and of course was without power, so my entertainment was that I watched their progress over the days. That convinced me that underground is not the answer to reliability.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
So, how deep would you have to go to make it unlikely someone would jam a backhoe into a 500kv line? If there was a fault to ground from one of these feeders, how wide an area would develop a lethal step potential?



I wouldn't worry about depth, because in any case you shouldn't go digging without having the area marked out prior.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
My neighborhood has 11kv underground feeds, they buried them under the sidewalks about 4’ down. The underground transformer for a big chunk of my neighborhood is in my yard and is basically under water whenever it rains. Apparently one on the connectors leaked one winter and allowed water to seep into the insulation where it eventually migrated down into the conductor. The result was an explosion that lifted the sidewalk concrete up about a foot in the air. It took a crew of 4 guys 4 days to fix it and test it, not counting the concrete crew that replaced the sidewalk. I was working from my home office at the time and of course was without power, so my entertainment was that I watched their progress over the days. That convinced me that underground is not the answer to reliability.


Radial always leaves a lot to be desired.

BTW, 4 days is incompetence, I've seen underground repairs done way faster.
 