In 590.6(A) Requires all 125-volt, single-phase, 15-, 20-, and 30-ampere receptacle outlets that are not a part of the permanent wiring of the building or structure and that are in use by personnel shall have ground-fault circuit interrupter protection for personnel, and does not permitting receptacles on lighting circuits. In NEC handbook?s commentary for 215.9 it states the following:
GFCI protection in the feeder can also be used to protect construction-site receptacles, as covered in 590.6(A), provided the feeder supplies no lighting branch circuits.
Section 525.23(C) does not permit egress lighting to be protected by a GFCI.
Section 620.24(A) Requires that hoistway pit lighting shall not be connected to the load side of a ground-fault circuit interrupter.
So how my question is temporary lighting circuit required to be or permitted to be protected a GFCI?
GFCI protection in the feeder can also be used to protect construction-site receptacles, as covered in 590.6(A), provided the feeder supplies no lighting branch circuits.
Section 525.23(C) does not permit egress lighting to be protected by a GFCI.
Section 620.24(A) Requires that hoistway pit lighting shall not be connected to the load side of a ground-fault circuit interrupter.
So how my question is temporary lighting circuit required to be or permitted to be protected a GFCI?