- Illinois
- retired electrician
Re: Temporary Service
Rick,
Don
Rick,
Article 450 has nothing to do with the overcurrent protection of transformer secondary conductors. It contains the rules for the protection of the transformer and only the transformer. The rules for the protection of the secondary conductors are found in 240.21(C). The same can be said for the original question. The rules for the required protection of a lighting and appliance branch circuit panel are found in Article 408 and not in Article 230.OK, In the true definition of service,these xfrmr conductors are not considered service conductors, they are feeder conductors by definition.However the overcurrent device is allowed to be as stated in (430.3(B)note 2.So in the case of xfrmr secondary conductors,either 1 MB or up to six with restictions.
I can't see why 408.36 excpt. #1 would'nt apply when 230.71 FPN is referring you to it when the service disconnect is a panelboard.whether the panelboard is fed from a feeder from a xfrmr secondary, or service conductors, the NEC is allowing it.
Don