Terminal Boxes
al
Minnesota
Section/Paragraph 230.82
Add:
230.82(9) Terminal boxes
Substatiation:
It is common practice to install terminal boxes on the supply side of service equipment. This change will make Article 230 consistent with the definition of Service Lateral in Article 100.
FYI: Because of the late date this has been sent in.
charlie
Indianapolis
Al, what is a terminal box? Where does the code define or use the term? I am making the assumption that it is a junction box, is that correct? Is this really correcting a problem? :)
al
Minnesota
Terminal Boxes
They are listed in the UL white book under(xckt)
Midwest is one of the mfgs:http://www.midwestelectric.com/
They are very common around here.
Al
charlie
Indianapolis
Interesting. I have never seen a termination box used anywhere. Does the code define or use the term? Should you also submit a definition of the term since (I believe) UL is the only entity that uses the term? :)
al
Minnesota
Charlie, look at the definition of Service Lateral.
Al
resistance
WA
My take is that Charlie is correct-- It's a Junction box! It's just a spruced-up name, because the box has pre-installed internal terminals for splicing conductors!
