I have done maybe 6 in Seattle with a permit, and never installed a lockout. A few of those were in sight, but I don't think it's required. To me that would be the same thing as picking sections out of article 422 for a transformer install. I don't see an EVSE being any more of appliance than a transformer is.
Well the lockouts are silly anyway for most brands like eatons so in all honesty it won't make any difference to someone who knows not to mess with it live.
If it's bonded at one end then you're good but if it was up to me I'd use an AC disconnect next to it and hit that with the mc and then thhn to the charger.
1. No need to use a breaker lock
2. Makes it easier to service in the future
3. Sell it as a safety disconnect and people like it
4. The KO in those chargers are so jambed in and the plastic so thick alot of connector don't have much bite on the locknut.
Why would you think a breaker lock would be required without the use of a disconnect here?? 625.43 is very clear on when a disconnecting means is required within sight of a hardwired evse or a breaker lock . And it’s only if the circuit is larger than 60 amps or 150 volts or more to ground
Hardwired EV needs a breaker lock if no other disconnect is within sight. Non issue If in the garage with the panel but that's not always the case
Not according to 625.43. A disconnect within sight of the evse or a breaker lock is only required for a hardwired evse if over 60 amps or 150 volts or more to ground . Hardwired evse 60 amps or less are not required to have a disconnect within sight
Yep your right. I still prefer the disconnect
Disconnects can come in handy. I don't really care about having a means of disconnect for an EVSE, but they are handy just as a splice or transition point. May allow you to run aluminum conductors for lesser cost, then transition to copper. A disconnect is often cheaper than a box and splicers. I have used them several times for this purpose.
I’ve used them as a point to transition From AL to cu conductors more than once as well on longer runs if not to have a negative effect on the aesthetics of the install . But I also know it’s not a requirement, I’m choosing to do it of my own accord not to satisfy the code. We are Tesla certified installers so I wire no less than 2-3 wall connectors every week , and I haven’t used anything but copper for at least 2 years and anytime I need to changeover from a cable assembly to conduit i feel using a metal 4 11/16” box is cleaner and less obvious than any disconnect . But over the last couple weeks I’ve hardwired two 80 amp evse (prime com tech) that required a 100 amp circuits per 625.41 so i had to provide a disconnect or a lockable breaker in accordance with 625.43
Hello All;
Can I terminate a run of 8/2 MC into a plastic EV charger enclosure?
While article 314 does not apply to an EVSE enclosure as its listed equipment I would check the manufacturers instructions. But in the absence of clear instructions I'd go by 314.3 as other UL standards for equipment pretty much say the same thing for OEM's;