Test prep question
nickelec
US
Need some input here on number 26 I think it's written very bad but I say .C could be b as well but the question is not indicating Ac snap of Ac/DC snap switch
Sent from my SM-G950U using Tapatalk
Here's the two sections with the relevant parts. You'll notice that there are two types of switches mentioned, AC only and AC/DC. For resistive loads the answer is the same so it doesn't matter whether you apply (A) or (B).
404.14
(A) Alternating-Current General-Use Snap Switch. A
form of general-use snap switch suitable only for use on ac
circuits for controlling the following:
(1) Resistive and inductive loads not exceeding the ampere
rating of the switch
at the voltage applied
(B) Alternating-Current or Direct-Current General-Use
Snap Switch. A form of general-use snap switch suitable
for use on either ac or dc circuits for controlling the fol-
lowing:
(1) Resistive loads not exceeding the ampere rating of the
switch
at the voltage applied.
Yes the answer is A based on the type of load mentioned in the question. Are all of the yellow highlighted answers correct?
Im the one with the highlither those are my answers so I'm hoping so
I just perused the other questions and was wondering what a T switch is in #23? Also I would check the answer to #25. :)
And I think I found that somewhere in 220
Yes article 220 is correct.
220.14(I) and (K) gives you 180VA per duplex receptacles.
210.21(B)(3) allows 2 or more 15A duplexs on a 20A branch circuit.
So you have a 20A circuit with duplexs calculated at 180VA per duplex......
I would say that most likely it is safe to assume 120V for the circuit.
Your right they got me with the wording 15A receptacles on 20A circuit