Testing an AFCI by arcing wires, and the UL test

Status
Not open for further replies.

PaulMmn

Senior Member
Location
Union, KY, USA
Occupation
EIT - Engineer in Training, Lafayette College
It's like outlet strips with surge protection being tested to "UL Standard #999--" And Standard #999 says "if it has a cord, the wire has to be insulated," or some such obvious standard! :)
 

kwired

Electron manager
Location
NE Nebraska
Yes, there is that.

Question is IMO, at what point does the mag trip overtake the electronica.
Mag trip is only looking at magnitude of current, electronics are supposedly looking at different signature patterns in that current and are supposed to object to any patterns that are not determined to be acceptable. May be a minimum overall current magnitude before this is supposed to apply.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Mag trip is only looking at magnitude of current, electronics are supposedly looking at different signature patterns in that current and are supposed to object to any patterns that are not determined to be acceptable. May be a minimum overall current magnitude before this is supposed to apply.

Yes, but we have electronica only because the mag trip can't be set to 75a.
 

kwired

Electron manager
Location
NE Nebraska
Yes, but we have electronica only because the mag trip can't be set to 75a.
Well then the mag trip takes precedence over electronics whenever that current level is reached, right?

Before AFCI came along, QO and Homeline had lower mag trip settings on standard 15 and 20 amp single pole breakers, this is why those often trip faster (whether desired or not) than other brands. Didn't necessarily make them better or worse just a different approach at circuit protection on those particular devices, which are the primary ones used for general use circuits.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
MOD C ! ! !

MOD C ! ! !

The graph, the Time - Current Response Curve, that RJ links to looks to be for a historic Branch Feeder type AFCI and that the graph is dated August 2002. I have serious doubts about the value of trying to use this response information with the GE MOD 3 Combination type AFCI.
 
Status
Not open for further replies.
Top