- New Jersey
- Journeyman Electrician (retired)
Yes you did I was simply agreeing with what you said.Short version of what I said, thanks.
Note that even this local amendment does not require the creation of a CEE where the design calls for a membrane between the foundation/footing and the substrate. It does not matter one way or the other is a membrane is installed only under the slab portion of the foundation. ...
"... when a new or replacement foundation or footing with a perimeter length of 6.0 m (20 ft.) or more is installed in direct contact with the earth."You read it differently than me, then. I read it as requiring a CEE to be installed, full stop. Thus, if a membrane would disqualify a CEE, then this section prohibits the membrane. I don't know from experience if the question has actually come up in SF.
I see. Maybe so."... when a new or replacement foundation or footing with a perimeter length of 6.0 m (20 ft.) or more is installed in direct contact with the earth."
That sure looks like an exception to me.
Right, but that only applies to existing buildings; the language requiring a CEE for new buildings has no such exception."... when a new or replacement foundation or footing with a perimeter length of 6.0 m (20 ft.) or more is installed in direct contact with the earth."
[Deleted previous comment.]Right, but that only applies to existing buildings; the language requiring a CEE for new buildings has no such exception.
So for new building, if you are required to create a CEE, but you want or need a vapor barrier under your footing, then you just need to cast a sufficiently large extra chunk of concrete directly against the earth, alongside your footing but outside your vapor barrier. No conflict.
Cheers, Wayne
Because they're being an idiot?Why would someone ask for a test showing MORE THAN 25 Ohms for a UFER?
Your inspector is way off on this! A CEE Does not require a 25 Ohms OR LESS resistance test.ALL, OP Here.
Just a little update. They went ahead and installed a UFER Ground because they have to pour concrete in an additional area of the home.
HOWEVER, the inspector is asking for a TEST on the UFER to prove there is MORE THAN 25 ohms. Does this make sense? There is only 1 area in the NEC that requires a ground test, but that test requires 25 Ohms or LESS and off memory, that only applies to ground rods to avoid a supplemental ground.
What a coincidence. I had the IDENTICAL theory. LMAOBecause he has numbers and Codes rattling around in his head like cue balls in a hard-sided suitcase, and he can’t make heads or tails of it all, so he spits out randomness like the little machine that ejects balls at the lottery drawing? Just my guess.![]()
Did he have a red nose and big black shoes on?Why would someone ask for a test showing MORE THAN 25 Ohms for a UFER?
HA. Yes, and rides around on an undersized bicycle.Did he have a red nose and big black shoes on?
I have never seen a slab on grade floor without the trenches for the footer at the edges. Is there such a thing as a slab on grade with no footer under the outside walls?What if it’s slab on grade with a vapor barrier?
Perhaps it is because the inspector knows their J O B and sees their job as actually enforcing the NEC as written.I haven’t updated my profile in 15 years. Also, somehow made it to post #13 prior to a code citation being mentioned.
I spoke with the building official and he agreed. Half of his inspectors were fine with 2 rods and the other half weren’t. Not sure why this 1 house this 1 time was an issue, but it was.