Here's a hint... it ain't the average of the 3 individual phase PF's!
Phil
So, how would you do it? And how would instantaneous values feature?
Which was my point.
Here's a hint... it ain't the average of the 3 individual phase PF's!
Phil
Leaving starting out of consideration and assuming a 100% efficient motor, so that the mechanical output power equals the electrical input power:
The engine (prime mover of the generator) needs to be able to produce 1kW continuously if you need the motor to work at full rated load. The one answer you ask for is (1).
The generator itself needs to source 1kW but also needs to be rated for 1.25kVA output (continuous).
100% efficient motor? so a motor with no R value, purely inductive? thus the ideal motor is an ideal inductor w/ fully loaded output (sounds like a xfrmer), and when unloaded the poco screams that their wires are melting. just cant win when it comes to power generation vs power consumption.
hold up, isnt efficiency tied directly to kVAR and R ? if my motor is just a big pure R then the e = 0 and kVAR = 0 (no mag field). in both cases each can have same amps thus looks like same load to the generator. if i have giant kVAR and zero R then its pure kVAR but there is no work done when there is no load on the motor (Rd=0). if i have just kVAR with R=0 then i am not wasting any watts, all the input in converted to output via mag coupling at a function Rd (Rd=0 then e=0 = no work done anywhere).If you do not specify an efficiency for your motor the question cannot be answered, since you list only the motor output.
I could have picked any efficiency and given the corresponding answer. I chose 100%.
If the efficiency of the motor is given by "e" and expressed in percent, then the power needed for the prime mover is 100/e kW and the generator must be able to source (100/e)(1.25) kVA.
Does that make you happier? The question still can not be answered by any of your four choices.
And, no a perfectly efficient motor would have no lumped constant R component but would still present a mostly resistive load to the generator because of what I will call the dynamic resistance, Rd, which converts input electrical energy into mechanical work. That effective Rd varies with the motor load.
An inductor with "a fully loaded output" is a very unfortunate way to try to describe it. It is in a sense a transformer though, in that it transforms electrical energy into mechanical energy, the input current depends on the output loading, and there is a purely reactive idling current when there is no load.
The engine (prime mover of the generator) needs to be able to produce 1kW continuously if you need the motor to work at full rated load. The one answer you ask for is (1).
The generator itself needs to source 1kW but also needs to be rated for 1.25kVA output (continuous).
hold up, isnt efficiency tied directly to kVAR and R ? if my motor is just a big pure R then the e = 0 and kVAR = 0 (no mag field). in both cases each can have same amps thus looks like same load to the generator. if i have giant kVAR and zero R then its pure kVAR but there is no work done when there is no load on the motor (Rd=0). if i have just kVAR with R=0 then i am not wasting any watts, all the input in converted to output via mag coupling at a function Rd (Rd=0 then e=0 = no work done anywhere).
In a word, NO.
The efficiency of a motor is by definition the ratio of output mechanical power to input electrical power.
The reactive portion of the input current does not correspond to input power. Period.
If there is no input and no output, then the efficiency is undefined and cannot be measured. If there is input an no useful output, then the efficiency is zero.
The efficiency losses resulting from bearing friction, air friction, and inductive losses in the rotor and stator material do not correspond to a measurable static R in the stator windings, but they are still there. And they can reduce the efficiency without reducing the power factor of the motor, since they still represent a purely resistive load.
BTW, Rd would be considered a parallel not a series resistance, so Rd = 0 is not a good thing. The efficiency would indeed be zero until the breaker opened, then it would once again be undefined. :angel:
what? math please.Assuming the motor, generator, and engine are perfect machines (meaning zero-losses) the generator providing 1kW @ 0.8pf to the motor, must also be rated 1kW @ 0.9pf, which equals 1.25kVA! However, the engine driving the generator must be rated 1kW, corresponding to 0.746Hp!
Phil
There may not be a motor with zero kVAR, but that has nothing to do with the efficiency of the motor.the only way to generate a mag field is via inductive kVAR. electrical amps to mag field to output power. so how is efficiency not tied to kVAR ?? please explain.
There may not be a motor with zero kVAR, but that has nothing to do with the efficiency of the motor.
what? math please.
Assuming the motor, generator, and engine are perfect machines (meaning zero-losses) the generator providing 1kW @ 0.8pf to the motor, must also be rated 1kW @ 0.9pf, which equals 1.25kVA! However, the engine driving the generator must be rated 1kW, corresponding to 0.746Hp! Phil
you are wrong phil, me a nuclear engineer and my early days of study were EE and CE, but those days have come and gone for me :thumbsup:EE-0001 when I went to school! Am I wrong in assuming you are an EE?
Phil
Fiona......please elaborate what the point is here.......for some this will look familiar and how it relates to the vector components of electrical power
you are wrong phil, me a nuclear engineer and my early days of study were EE and CE, but those days have come and gone for me :thumbsup:
but my question is still valid, pls show the math from your EE-0001 class.
edit: i see from your last post that you corrected your statement.
and as a side note, kVAR is like a short to a generator, take a pure inductor and lower the frequency, amps will approach infinity.
just a graph of what a generator may look like when kVAR becomes very large. no need to get any deeper than that, beyond the scope of this discussion.Fiona......please elaborate what the point is here.......
a good efficient motor has no R and lots of inductive kVAR, and when you load the motor the kVAR turns into watts. if we want to use the basic nomenclature, potential to kinetic energy, etc.
[/B]
That is a very simplistic and very misleading statement.
First, it implies that the eventual wattage cannot be greater than the unloaded kVAR. (It does not say that, but I am afraid some will draw that conclusion.)
Second, it implies that the kVAR goes down as the motor is loaded. In fact the PF improves as the motor is loaded mainly because the resistive component goes up. The kVAR does not need to go down for the PF to improve (although it might).
And the analogy to the relation between potential and kinetic energy is just flat out wrong and therefore not particularly useful in understanding what is happening.