Volt-Amperes does not directly equal Joules per second.
what? it totally does. the definition of watt is not the same as "power dissipated" (aka "consumed"). if i take 10200eV and move it from inductor to cap via wire with zero R, i move it via watt units yet no power is consumed.

eV is a better unit to use when we get closer to what is really going on from the physics view.

This is an incandescent bulb filmed in slow motion, with a 50 Hz AC power source. You can see that the power is not steady, but instead comes in cycles. So the Wattage rating on the bulb, is really the average Watts over a cycle.
https://www.youtube.com/watch?v=eUprJS9sXYU

what you see is not what you get? if you place a sensor on generator shaft to monitor magnetic impulse jitter, does it match the frequency of the bulb filament as seen in that video? you tell me.
 
Last edited:

Carultch

Senior Member
Location
Massachusetts
what? it totally does. the definition of watt is not the same as "power dissipated" (aka "consumed"). if i take 10200eV and move it from inductor to cap via wire with zero R, i move it via watt units yet no power is consumed.

eV is a better unit to use when we get closer to what is really going on from the physics view..


Here's a similar idea.

Suppose you have a rectangle. We all know that the area is length*width.

Now suppose you have an irregular shape that is sort of rectangular. But it is irregular enough to matter. You can establish a bounding box to enclose this shape, to get a representative length and width. However, if you multiply the representative length and the representative width together, should you expect that you can calculate the area this way? You might get a good guess, but you will not accurately calculate the area by only accounting for representative length and width.

Volt-amperes work the same way. The inherent problem is that we are multiplying time "average" values of voltage and current, and expecting them to calculate power. In reality, it is only valid to calculate power by multiplying Volts and Amps, when you multiply the instantaneous voltages and currents that occur simultaneously. Multiplying time "average" values overlooks the phase shift and other irregularities.
 
Last edited:

Besoeker

Senior Member
Location
UK
In reality, it is only valid to calculate power by multiplying Volts and Amps, when you multiply the instantaneous voltages and currents that occur simultaneously.
And you get instantaneous power for that instant in time which isn't terribly useful for most purposes.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Volt-Amperes does not directly equal Joules per second.
what? it totally does.

You need to reread the rest of Carultch's post.

Instantaneously Volts * Amperes = Joules /second. So if you integrate Volts * Amperes over time, you will get real power integrated over time, or energy transferred. That is, you need to multiply first, then "average".

However, as a communications convention, when we choose to write VA instead of Watts, that means we are multiplying two "averages". Since we "averaged" first, before multiplying, we don't get the real power.

Cheers, Wayne
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
Here's a similar idea.

Suppose you have a rectangle. We all know that the area is length*width.

Now suppose you have an irregular shape that is sort of rectangular. But it is irregular enough to matter. You can establish an average length and an average width. However, if you multiply the average length and the average width together, should you expect that you can calculate the area this way? You might get a good guess, but you will not accurately calculate the area by only accounting for average length and average width.

Volt-amperes work the same way. The inherent problem is that we are multiplying time "average" values of voltage and current, and expecting them to calculate power. In reality, it is only valid to calculate power by multiplying Volts and Amps, when you multiply the instantaneous voltages and currents that occur simultaneously. Multiplying time "average" values overlooks the phase shift and other irregularities.

well, you say "Suppose you have a rectangle. We all know that the area is length*width."
no we do not, at least not by physics! you could only find scalar for a instantaneous observation, after that observation the area has changed :D
the physics says no such thing, you cannot create a true/fixed LxW rectangle in the physical world (it would indeed be a jagged rectangle when you look close, and would actually be changing shape with any delta t). if you wish to stay in math only then you are no longer using physics.
 

Carultch

Senior Member
Location
Massachusetts
well, you say "Suppose you have a rectangle. We all know that the area is length*width."
no we do not, at least not by physics! you could only find scalar for a instantaneous observation, after that observation the area has changed :D
the physics says no such thing, you cannot create a true/fixed LxW rectangle in the physical world (it would indeed be a jagged rectangle when you look close, and would actually be changing shape with any delta t). if you wish to stay in math only then you are no longer using physics.

You are making up red herrings to intentionally miss my point.
 

Besoeker

Senior Member
Location
UK
True. But your next step is intuitively obvious. Take the average value of that instantaneous power, which is the power we use in most purposes.
And taking that a step further, we don't normally use instantaneous values of volts and amps either.

Sqrt(3)*VL*IL*cos(phi) with RMS values for V and I is how most of us would do it for three phase systems.

Somehow, this thread has served to complicate that simple formula out of all proportion.
 

Carultch

Senior Member
Location
Massachusetts
And taking that a step further, we don't normally use instantaneous values of volts and amps either.

Sqrt(3)*VL*IL*cos(phi) with RMS values for V and I is how most of us would do it for three phase systems.

Somehow, this thread has served to complicate that simple formula out of all proportion.

How does it work when each phase has a different power factor and value of phi?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
At some point what was physics becomes philosophy, but then doesn't everything? :D
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Here's a hint... it ain't the average of the 3 individual phase PF's!

Phil

If you had exactly matched leading and lagging PFs on two phase lines and a PF of 1 on the third line the "overall" PF (kW/kVA) might end up as 1 but POCO would still treat it as an non unity PF when calculating for possible penalties. Just how to calculate the kVA term could be a little difficult when combining leading and lagging kVARs.

The "average" of a leading PF of .8 and a lagging PF of .8, on the other hand, would be .8, and for some purposes that would be a good measure of the reactive nature of the load(s).

I do not see a simple, one size fits all, measure that fully represents such a single or three phase circuit.
When dealing with an unbalanced PF load, I wonder just how the POCO meter captures kVA for the purposes of demand penalty?
Simple sum of kVA over all phases with no consideration of leading or lagging?
 

FionaZuppa

Senior Member
Location
AZ
Occupation
Part Time Electrician (semi retired, old) - EE retired.
but i ask again, a different way

i have a motor that says 1kW output, PF=0.8

i now wish to build my generator/engine so that my motor can do the work i need it to. how much kW (approx) does the generator/engine need to produce assuming the motor leads are directly attached to the generator leads (no wire between)?

1) 1kW
2) 1.25kW
3) 1.5kW
4) 0.8kW
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
but i ask again, a different way

i have a motor that says 1kW output, PF=0.8

i now wish to build my generator/engine so that my motor can do the work i need it to. how much kW (approx) does the generator/engine need to produce assuming the motor leads are directly attached to the generator leads (no wire between)?

1) 1kW
2) 1.25kW
3) 1.5kW
4) 0.8kW

Leaving starting out of consideration and assuming a 100% efficient motor, so that the mechanical output power equals the electrical input power:

The engine (prime mover of the generator) needs to be able to produce 1kW continuously if you need the motor to work at full rated load. The one answer you ask for is (1).
The generator itself needs to source 1kW but also needs to be rated for 1.25kVA output (continuous).
 