There are two problems with saying that:the kVAr's are indeed just lost power.
1) While the VArs do represent power shuttling back and forth through the transmission system, the only loss associated with them is the transmission losses from the additional current, primarily the additional I^2*R heating losses. That loss will be a small fraction numerically of the VArs.
2) The value of VArs does not represent an actual 'rate of transfer of energy' at any point in the system over any natural period of time. For example, the amount of energy transferred over a quarter cycle (and soon to be returned over the next quarter cycle) by 1 VAr is 2/pi times the amount of energy transferred over a quarter cycle by 1 Watt of real power. (see math below)
Cheers, Wayne
The integral from 0 to pi/2 of sin(t)cos(t) is 1/2. The integral from 0 to pi/2 of sin(t)sin(t) is pi/4. The ratio is 2/pi.