FionaZuppa, here's an example like yours:
Say we have a voltage source of 100V with an internal resistance of 0.001 ohms, connected via transmission wires with a resistance of 0.2 ohms, to a load. Consider two different loads with (almost) the same active power:
a) A pure resistance of 9.8 ohms. The transmission plus load resistance is 10 ohms, so the current is 10 amps. The load power is I^2 R = 980 watts. Transmission losses are 20 watts, and the internal generator resistance dissipates 0.1 watts. The input power to our voltage source is 1000.1 watts. The electrical efficiency of the system is 980/1000.1 = 98.0%
b) A load with resistance 4.9 ohms and reactance 4.9 ohms, so the impedance is 4.9 sqrt(2) ohms = 6.93 ohms. The transmission plus load impedance is 7.07 ohms, so the current is 14.14 amps. The load power is I^2 R = 979.6 watts (and the load reactive "power" is 979.6 VAr). Transmission losses are now 40.0 watts, and the internal generator resistance dissipates 0.2 watts. The input power to our voltage source is 1019.8 watts. The electrical efficiency of the system is 96.1%.
So yes, when the load changes from (a) 980 watts + 0 VAr to (b) 979.6 watts + 979.6 VAr (apparent power 979.6 * sqrt(2) = 1385 VA), the input power goes up. However, it doesn't go up by a factor of 2, or a factor of sqrt(2). Rather the system losses basically double from 2% to 4%.
Cheers, Wayne
Say we have a voltage source of 100V with an internal resistance of 0.001 ohms, connected via transmission wires with a resistance of 0.2 ohms, to a load. Consider two different loads with (almost) the same active power:
a) A pure resistance of 9.8 ohms. The transmission plus load resistance is 10 ohms, so the current is 10 amps. The load power is I^2 R = 980 watts. Transmission losses are 20 watts, and the internal generator resistance dissipates 0.1 watts. The input power to our voltage source is 1000.1 watts. The electrical efficiency of the system is 980/1000.1 = 98.0%
b) A load with resistance 4.9 ohms and reactance 4.9 ohms, so the impedance is 4.9 sqrt(2) ohms = 6.93 ohms. The transmission plus load impedance is 7.07 ohms, so the current is 14.14 amps. The load power is I^2 R = 979.6 watts (and the load reactive "power" is 979.6 VAr). Transmission losses are now 40.0 watts, and the internal generator resistance dissipates 0.2 watts. The input power to our voltage source is 1019.8 watts. The electrical efficiency of the system is 96.1%.
So yes, when the load changes from (a) 980 watts + 0 VAr to (b) 979.6 watts + 979.6 VAr (apparent power 979.6 * sqrt(2) = 1385 VA), the input power goes up. However, it doesn't go up by a factor of 2, or a factor of sqrt(2). Rather the system losses basically double from 2% to 4%.
Cheers, Wayne