rabtrfld
Member
- Location
- Milwaukee, Wisconsin
We have some scrap 8/3 UF-B, can we remove the jacket and use the wires as THHN?
rabtrfld said:We have some scrap 8/3 UF-B, can we remove the jacket and use the wires as THHN?
infinity said:Do we know for sure that it's not marked on the individual conductors? People say this about MC cable all of the time but lately I've seen MC with marked conductors.
So you use THHN for your tails inside the device boxes, or do you use little bits and scraps harvested from the MC or NM?Jim W in Tampa said:have never seen mc stamped other than the clear plastic wrap around it.No marking then scrap it out.
mdshunk said:So you use THHN for your tails inside the device boxes, or do you use little bits and scraps harvested from the MC or NM?
mdshunk said:So you use THHN for your tails inside the device boxes, or do you use little bits and scraps harvested from the MC or NM?
You too?peter d said:I use pieces of TW circa 1965.
Jim W in Tampa said:have never seen mc stamped other than the clear plastic wrap around it.No marking then scrap it out.
Is this the new MC AP cable where the neutral is marked to indicate the cable armor is equipment grounding conductor path?infinity said:Do we know for sure that it's not marked on the individual conductors? People say this about MC cable all of the time but lately I've seen MC with marked conductors.
tom baker said:Is this the new MC AP cable where the neutral is marked to indicate the cable armor is equipment grounding conductor path?
infinity said:I guess that you're referring to MC-ap. No, this is standard MC cable with an insulated EGC and each conductor marked.