stickboy1375 said:IMO everything is subject to damage...![]()
True enough.
Glad your not yet an inspector.
stickboy1375 said:IMO everything is subject to damage...![]()
stickboy1375 said:Why do we even use the NEC if an installation is good in one state but yet not another? Your state accepted the 2005 nec correct? They why would that installation not pass?
dcspector said:The SE must be protected 230.50?
dcspector said:and what state are You referring to?.....DC is still under the frigin 96? I am tested to 05 and You think that SER connector is a DRY location Damp ain't gonna happen ? Also, The SE must be protected 230.50? So what are You sayin ?
230.50 Protection of Open Conductors and Cables Against Damage ? Above Ground.
Service-entrance conductors installed above ground shall be protected against physical damage as specified in 230.50(A) or (B).
(A) Service Cables. Service cables, where subject to physical damage, shall be protected by any of the following:
(1) Rigid metal conduit
(2) Intermediate metal conduit
(3) Schedule 80 rigid nonmetallic conduit
(4) Electrical metallic tubing
(5) Other approved means
dcspector said:and what state are You referring to?.....DC is still under the frigin 96? I am tested to 05 and You think that SER connector is a DRY location Damp ain't gonna happen ? Also, The SE must be protected 230.50? So what are You sayin ?
dcspector said:Trevor......it is subject to physical damage. What are the limitations of damage on an exposed SER?...not much..IMHO
dcspector said:Trevor......it is subject to physical damage. What are the limitations of damage on an exposed SER?...not much..IMHO
And I work in PA, MD, and DE, and it's a normal install there too.iwire said:Trevor sees this in NJ, Stick is from CT, I work in MA, RI and CT.
dcspector said:Stickboy........I said Damp....Are we cool?
iwire said:Here is a very typical multifamily house service around here.
![]()
mdshunk said:Got interior pics?
I'm curious on how that 6th can receives its line side conductors.......Just wondering if they bolted mechanical lugs on those buss bars or what.
(or if that's even permitted)
Looks like someone didn't want to spring for a 6 gang 200 amp can, when all they needed was 5-100's and 1-200
Ah.. I see. 'Round my parts, most of the POCOs want at least horn bypass for everything, so the supply houses don't even stock meter cans without horn or lever bypass provisions.iwire said:So it's not that my buddy needed a 200 amp socket, he needed a bypass version.
iwire said:I don't think any of the local POCOs accept horn bypass, all seem to want lever.
I never heard of a horn bypass until someone said it on a forum.