Hold-down hardware?
That panel predated that requirement.
Hold-down hardware?
Yeah, that's probably what it comes down to, right? It seems people need pics:
View attachment 21477View attachment 21478
well at least one pipe has a overloaded neutral, and that's without clearly seeing all terminations... 11 breakers and 10 hots- and 4 nu=eutrals… not good
well at least one pipe has a overloaded neutral, and that's without clearly seeing all terminations... 11 breakers and 10 hots- and 4 nu=eutrals… not good
I'm looking to see if there's consensus on whether the panel itself is a no-no.
I can only see three of the conduits coming in, not counting the feeders. They each look normal, figuring likely MWBCs.
Next person trying to add something might have more to look at than just single or three phase. Even if it were supplied with three phase, doesn't mean they can add any load, still need to see if there is capacity for what they are adding. Not going to add a 100 kVA load to a 100 amp 208/120 panel and have it operate successfully.This might be a code violation (AND a hazard) if it's a service entrance and the B-phase conductor is "protected" by two breakers in parallel, which would allow double the B-phase conductor's ampacity to flow before tripping.
Even if not, it seems like a really bad idea. The next person to come along and add something will face several non-obvious opportunities for trouble. For example:
- The above-mentioned shared-neutral MWBC, which will seem to be OK when installed & tested but will eventually overheat the neutral.
- Trying to supply a three-phase device from this "three-phase" panel, which won't work and might damage a motor.
- Trying to supply a 208-volt single-phase load from the B & C phases, which won't work.
- Trying to supply a 208-volt single-phase load from the A & B phases, which might overheat on 240 volts, ...
At worst, the next person trying to add something might place a hex on the original installer, resulting in a lifetime of bad luck and torment.
(sorry, watching too many old Halloween Week movies)
That section requires it be marked with voltage/current rating and number of buses, doesn't say you must use a panel with three ungrounded buses for three phase supply.To me, this panelboard would be a violation of 408.58.
This panel is being used for a different number of phase conductors than for what it was designed.
JAP>
That section requires it be marked with voltage/current rating and number of buses, doesn't say you must use a panel with three ungrounded buses for three phase supply.
If you need single phase or even two wire DC and are using an I line panel - you get a panel with three buses as that is all they make in that series. You just don't use one of the buses and order breakers that don't connect to the unused bus.
What about my mentioning of I -Line panels? They all have three buses, but if you need single phase or even two wire DC you just don't use one of the buses.Actually that section requires it to be marked for the number of "Phases" not the number of "Buses".
There is not 3 phase inside the panel as the cover would suggest, therefore I would consider it a violation of this rule.
JAP>
What about my mentioning of I -Line panels? They all have three buses, but if you need single phase or even two wire DC you just don't use one of the buses.
Not sure what actual markings on equipment says but looking in Square D catalog NQ panels are rated for 240 volts AC as well as 48 volts DC. Not seeing 48 VDC in the load center section of catalog, but seem to recall seeing that rating in the field.
Just because there are three buses doesn't necessarily mean you must use them or that you must supply them with "three phase". I think. Main thing is not to exceed maximum rated voltage and current.
Might be good design to make field markings of what is in there if not what one would typically expect.
One can go down similar path when it comes to presence of a grounded conductor bus in the assembly. For services you must run the grounded conductor, but for non service applications you don't need to run a grounded conductor if there is no loads utilizing a grounded conductor. Rarely have done this with 120/240, but has been a time or two where using a panelboard supplying straight 240 only loads. Done it even more often with 480/277 when there are no 277 volt loads - mostly just motors or other "power" loads.
A suitable 1ph panel can be bought for under $100, so I don't see the reason to keep this one.
Not in the vocabulary of a cheapskateA suitable 1ph panel can be bought for under $100, so I don't see the reason to keep this one.
A suitable 1ph panel can be bought for under $100, so I don't see the reason to keep this one.
This topic is similar to using typical 120/240 panel on a 120 volt only supply line. It does happen occasionally, but they don't really make a panel designed specifically for just 120 volt two wire supply.
So is labor, knowing what to use and how to use it is expensive:happyyes:Materials are the cheapest part of the job.