Gee whiz, I walk away for one night and the details start flowing in. :) Many thanks for the input. But I am going to have to spend some time digesting your comments, before I can respond. I will say, in answer to someone's question, that a single enclosure (bigger than a bread box, but not quite as large as an SUV) contains the transformer, conductors from the secondary to bus bars, the bus bars themselves, and four breakers, and it is manufactured and listed as a single entity. That at least is my understanding. I have not seen it yet.
 

Smart $

Esteemed Member
Location
Ohio
Gee whiz, I walk away for one night and the details start flowing in. :) Many thanks for the input. But I am going to have to spend some time digesting your comments, before I can respond. I will say, in answer to someone's question, that a single enclosure (bigger than a bread box, but not quite as large as an SUV) contains the transformer, conductors from the secondary to bus bars, the bus bars themselves, and four breakers, and it is manufactured and listed as a single entity. That at least is my understanding. I have not seen it yet.
IMO, manufactured and listed as a single entity removes it from the purview of the NEC, except for 110.2 Approval.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
IMO, manufactured and listed as a single entity removes it from the purview of the NEC, except for 110.2 Approval.
That occurred to me as well.


Here (or so I believe) is a photo of the item in question. It was taken during a field trip by another engineer working on the project.

IMG_6631.jpg
 
Last edited:

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
OK, I have reviewed what several of you have been saying, and I think I see the issues. Let’s assume the NEC does apply here, and let me try the following approach.

? There is a set of “secondary conductors” that connects to the center of the transformer’s secondary windings. They are less than 3 meters long.
? The other end of these secondary conductors connects to a device that I will call a “switchboard” (i.e., what I have previously been calling "bus bars").
? The secondary conductors do not extend beyond this switchboard.
? Their ampacity exceeds the rating of the switchboard, and also exceeds the load current.
? I don’t need a raceway to enclose the secondary conductors from the location of the transformer to the location of the switchboard, as they in the same enclosure as the switchboard.
? I am now in a 240.21(C)(2) situation. Please note that that article does not require the secondary conductors to terminate at an OCPD.

Conclusion: This is code compliant. Whatcha tink?
 

Smart $

Esteemed Member
Location
Ohio
OK, I have reviewed what several of you have been saying, and I think I see the issues. Let?s assume the NEC does apply here, and let me try the following approach.

? There is a set of ?secondary conductors? that connects to the center of the transformer?s secondary windings. They are less than 3 meters long.
? The other end of these secondary conductors connects to a device that I will call a ?switchboard? (i.e., what I have previously been calling "bus bars").
? The secondary conductors do not extend beyond this switchboard.
? Their ampacity exceeds the rating of the switchboard, and also exceeds the load current.
? I don?t need a raceway to enclose the secondary conductors from the location of the transformer to the location of the switchboard, as they in the same enclosure as the switchboard.
? I am now in a 240.21(C)(2) situation. Please note that that article does not require the secondary conductors to terminate at an OCPD.

Conclusion: This is code compliant. Whatcha tink?
Sounds good to me... :D
 

RUWired

Senior Member
Location
Pa.
i agree as well now that i have been enlightend from Smart$ about devices.

Now that the secondary conductors are protected, have you solved the problem with protecting the secondary of the transformer. (1935 amps vrs. 1800 amps)
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Now that the secondary conductors are protected, have you solved the problem with protecting the secondary of the transformer. (1935 amps vrs. 1800 amps)
Still working on that one. If you look at the photo from post 45 above, and see the type of building served by this substation, it becomes a murky question as to whether this can be called a "supervised location," in the context of Table 450.3(A). But that is being discussed in another thread, here: