Would it, perhaps, be more accurate to say that overcurrent protection is required, and that it can consist of up to six breakers (i.e., you don't need a single main breaker)? The design I am reviewing has four breakers connected to the bus bars, and all of it (including the transformer) is enclosed within this outdoor substation.
Yes it would be more accurate to say that. I was thinking the "secondary conductors" would not be protected because 240.21 doesn't mention multiple devices even though the "transformer secondary" would be protected with the up to 6 breakers.