Tied to ground? What does this mean? (transformers)

Status
Not open for further replies.

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
No, it is not showing the high side delta winding is corner grounded.

This is a diagram of a normal (North American Standard), delta primary, wye secondary, transformer. Exactly what one would use for 13.8kv/480V Y transformer.

One certainly would not corner ground a primary delta.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Corner grounded delta would be my guess. Not that I've come across any here in UK.
No.

The corner ground symbol would be outside of the delta and contain a 'ground' symbol.

Because this is a dashed line internal to the delta, it provides information on the angle/relationship of the windings. It is used with a comparable dashed line on the diagram of the secondary. I believe the typical wye secondary dashed line is hidden by the neutral point grounding symbol.
 

Besoeker3

Senior Member
Location
UK
Occupation
Retired Electrical Engineer
No.

The corner ground symbol would be outside of the delta and contain a 'ground' symbol.

Because this is a dashed line internal to the delta, it provides information on the angle/relationship of the windings. It is used with a comparable dashed line on the diagram of the secondary. I believe the typical wye secondary dashed line is hidden by the neutral point grounding symbol.
I apologise and stand corrected.
 