To Bond or not to bond/

Status
Not open for further replies.

sjac

Member
Location
oklahoma
I am wiring a house on a farm, the feeder comes from a 200 amp panel at the service pole, do I bond the neutral and ground in the main house panel or not?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The short answer is "no". 547.9 & 250.32 & 250.4 are applicable.
If this is an existing situation, the exception to 250.32 might apply.
 