S sjac Member Location oklahoma May 15, 2015 #1 I am wiring a house on a farm, the feeder comes from a 200 amp panel at the service pole, do I bond the neutral and ground in the main house panel or not?
I am wiring a house on a farm, the feeder comes from a 200 amp panel at the service pole, do I bond the neutral and ground in the main house panel or not?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 15, 2015 #2 The short answer is "no". 547.9 & 250.32 & 250.4 are applicable. If this is an existing situation, the exception to 250.32 might apply.
The short answer is "no". 547.9 & 250.32 & 250.4 are applicable. If this is an existing situation, the exception to 250.32 might apply.
Sierrasparky Senior Member Location USA Occupation Electrician ,contractor May 15, 2015 #3 Feeder needs a neutral and ground.