Too much bonding

Status
Not open for further replies.
In the field with no code book, discrepancy on bonding ,grounding. At a existing home a 200 amp panel fed from a transfer switch proper bonding with the grounding and grounded conductor is at the Meater main , the problem I see is they are bonding neutral to ground at the panel also , code references would be helpful thanks !



Sent from my iPhone using Tapatalk
 
In the field with no code book, discrepancy on bonding ,grounding. At a existing home a 200 amp panel fed from a transfer switch proper bonding with the grounding and grounded conductor is at the Meater main , the problem I see is they are bonding neutral to ground at the panel also , code references would be helpful thanks !



Sent from my iPhone using Tapatalk

This is a violation of 250.24(A)(5).
 
Thank you that's I told them , just didn't have the reference to back it thanks


Sent from my iPhone using Tapatalk

Getting the PDF version of the NEC on your phone is invaluable in those situations....unless you know it by memory:angel:
 