The posts 45-47,49&52 show how grounding may also protect LV installations.
The posts 45-47,49&52 show how grounding may also protect LV installations.
K8MHZ: First state whether any shock experienced in a residence due to upstream neutral break.
Consider a 14.5Kv single phase primary with neutral grounded and 240/120V secondary with neutral not grounded POCO transformer. Also suppose no grounding downstream with insulated EGC. Under these circumstances hazardous voltage may be present on the secondary load side depending on the capacitances between primary and secondary, secondary and ground. But if secondary side is grounded, such hazardous voltage disappears.
It sounds like you are describing an ungrounded system, with no grounding electrode connected to the non current carrying metal parts. In this situation, I still see the grounding electrode as providing a very minor role. You would still need everything bonded together to reduce touch potential between metal parts, allow ground fault detectors to function, and provide a low impedance path for a second fault. If you have that done, I highly doubt that bonding system will not have been already "accidentally" bonded/referenced to ground through pipes, attachment to concrete, direct contact, etc.
K8MHZ: The electrician was on the metal post. If earth link was grounded, it and the metal post would be at same potential (as metal post was also fixed to ground), no matter whether any load current flowing in overhead neutral line or not and so the electrician would not have received a shock.
If you look through the lens of the code, you would see the solution to avoid the accident mentioned in post # 45 contains a code violation, which K8MHZ also missed.
What is it?
There were at least two grounds one formed at metal post and other by grounding the shorting earth link (per accident prevention suggestion in post 45). But per code there shall be only single ground. So the grounds were to be bonded together in addition to avoid shock to electriccan on post. I got this insight by discussion in forum. Thanks.If you look through the lens of the code, you would see the solution to avoid the accident mentioned in post # 45 contains a code violation, which K8MHZ also missed. What is it?
There were at least two grounds one formed at metal post and other by grounding the shorting earth link (per accident prevention suggestion in post 45). But per code there shall be only single ground. So the grounds were to be bonded together in addition to avoid shock to electriccan on post. I got this insight by discussion in forum. Thanks.
K8MHZ: Note in post 46 of 'not grounded' refers to earth link and not metal post. Sorry again for poor quality of drawing. Also I might have used 'single ground reference' instead of simply saying 'single ground'. Note a person is liable to get a shock when he stands on ground and in contact with metal surface of a system under fault which is bonded but not grounded.
..... Note a person is liable to get a shock when he stands on ground and in contact with metal surface of a system with phase fault to metal surface which is bonded but not grounded.
You have it backwards.
Back to square one. See post 26.He does.Sahib, if the metal pole was bonded properly back to the source thru the egc, the breaker would have opened already and de-nergized the ckt, thus preventing the employee from getting shocked in the first place. Adding a ground rod or 2 or 3 to the base of that pole would not help a thing in the absence of bonding.Pay attention to the pics that K8MHZ posted.
Back to square one. See post 26.
In remote locations where OCPD/ground fault protector such as GFCI becomes ineffective for shock protection due to long circuit length/high ground resistance, ground fault protection in that case may be made effective by decreasing the ground resistance with a ground rod so that enough leakage current flows through ground fauit protector device to operate it.
If you don't have enough current flow to trip a GFCI you don't have a serious shock hazard.
Truthfully if the circuit is so long it needs an electrode to help the GFCI operate it would be hard to get a shock from the circuit in the first place.