rekjr_mgs
Member
- Location
- Minneapolis, MN USA
Working on a new piece of equipment that will go into a Class II Division 1 Group EFG Hazardous Location. The previous non-HL unit that this new one is based on had an A-B PanelView 1000. We'd like to stick with this solution since the program is already written but are getting conflicting info back from A-B re: the suitability of this unit to the environment. We are planning on putting it in the door of a non XP enclosure (NEMA ??) with a P&F type Z purge unit. If it matters, this enclosure is separate from the main electrical enclosure and should only contain the 24VDC HMI and perhaps some Intrisically Safe pushbuttons. On one hand A-B says it is rated for the purge pressure but can't seem to confirm whether it still will meet Class II Div 1 when installed as specified. Anyone with experience similar to this for this environment? Does it make sense that, while a device that is mounted to the exterior skin of a purged enclosure can tolerate the pressure, it still does not actually meet the appropriate spec? Thanks in advance for the help!