wirebender said:IMSO this won't fly. 2008 says "In all areas specified in 210.52", not "all receptacles required by 210.52".
If an area is specified in 210.52, and I don't think it misses any areas of a residence, then receptacles in that area must comply.
Edit to add: Maybe attics would be okay.
I agree 100%!! the code says 'in all areas specified in 210.52. so if its in the area It has to be tamper resistant. The thing is i have yet to see both Tamper resistant and weather resistant GFCI receptacle. they have the 'tamper resistant GFCI , and they have the Weather resistant GFCI, but to comply with the code in a dwelling (outside) then it has to be Both Tamper resistant and weather reistant at the same time GFCI.