The listing of the product, listed as suitable for services, permits a service rated transfer switch to be installed in such a manner.
110.3(B)
NEC 230.83 does not mention transfer switches on the supply side of the service disconnect. I am confused
The transfer switch needs to have an over current protection device in it for the service conductors to land in first and it also has to be indicating showing the on or off position.
OK meter - tranfer switch - main switch normal power.
Generator - Gen oc ( non seperately derived system) - transfer switch - main switch.
can generator feeders go thru meter?
Should be meter,main,transfer switch. No the generator feeders cannot go through the service conductors meter.
I agree ,but need code reference to enforce. THe generator feeder is 230.7
If the transfer switch is service rated, why would a main be needed on the line side of the transfer switch?Should be meter,main,transfer switch. No the generator feeders cannot go through the service conductors meter.