Phasing is all correct. I think the phase differential is 30 degrees. I was just guessing at 20-25 degrees based on the graph on the 'scope. It now makes sense to me that the transformers involved would cause that differential. This is, indeed, an ASCO switch. The problem I have is that even when the generator comes on after a loss of utility power, the ASCO switch doesn't transfer. The indicator light on the in-phase monitor shows that's it's ready to transfer, but for some reason won't make the transfer.
I am jumping in here after breezing thru all the posts so bear with me.
How are you testing the ASCO? If you are using the test switch then it is a hot-bus, hot bus transfer and the inphase monitor (synch check relay) is active. You will need a difference of 0.1 to 0.2 HZ between the gen and utility to get a timely transfer. If the F of the gen is dead on 60.00HZ then it may or may not transfer at all because the sweep time between voltages is too slow. I get a lot of calls because of this because the gen techs insist on exactly 60.0000000HZ!! As you increase the speed (HZ) of the gen then the sweep time increases and once the phase angle between the voltages becomes less than around 10 degrees is should transfer.
Now, if you are doing the test by opening the normal source breaker (dead-bus, hot-bus) then the synch check is not active and defaults to allow transfer because like other posts indicated, you are not comparing sources. In this case the phase angle argument goes out the window.
You said the light on the inphase monitor stays on then it sounds like you
are testing by opening the breaker. If this is the case the problem is elsewhere. A 15yr old ASCO without the proper maintenance is prone to failure. The factory grease dries up and the transfer mech becomes sluggish
preventing transfer. Manually transfer it and if it feels tight, clean & relube.
Check the solenoid coil resistance, it may be open. Good luck.
one more thing, shut the switch down, manually transfer it to emergency, and then close the normal breaker. If it transfers to normal then the coil is good.